Sure it has to do with engineering issues.

The reason I became suspicious of the true nature of the events was because the explanations that fire caused these collapses did not work engineering wise.


Why not? Do you believe fire cannot cause structural elements to fail?

The freefall acceleration of WTC 7 and continuous acceleration of the North Tower are clear and unambiguous indications of unnatural causes.


Do you understand that when a hyperstatic structure becomes an unstable mechanism (after successive elements failures) there's no significant resistance anymore?

Continuous acceleration of the North Tower? Really? So, why was the collapse time greater than FFA time?
 
Continuous acceleration of the North Tower? Really? So, why was the collapse time greater than FFA time?

In all fairness, the Truthers at least understand that the towers fell at less than FFA. However, they tend to follow Chandler's vastly misguided lead and equate the average acceleration with the instantaneous acceleration, which is completely off the mark.

ETA: They also do the same thing with WTC7, equating the average "approximately FFA" of the initial collapse stage with the actual wildly fluctuating acceleration values. It's like Truthers can't understand the concept of an average and the situations in which it is appropriate to use the average.
 
Last edited:
Sure, considering he held a paper mask to his face and told people to run away from a giant rolling dust cloud and then proceeded to make millions off talking about it, I'd say he made out like a bandit.

And the friends he lost that day? Just the cost of doing business I guess.

Edited by kmortis: 
Removed personal comment.
 
Last edited by a moderator:
Why not? Do you believe fire cannot cause structural elements to fail?

Yeah, that's right. Twoofers believe that fire can't cause structural elements to fail. You nailed it.


Do you understand that when a hyperstatic structure becomes an unstable mechanism (after successive elements failures) there's no significant resistance anymore?

Oooo... Hey everyone, Carlos here can tell us how structural redundancy engineered throughout a 47-storey steel-framed highrise became an "unstable mechanism". Finally! Oh boy! I'm looking forward to hearing this explanation!


Continuous acceleration of the North Tower? Really? So, why was the collapse time greater than FFA time?

Yaaah, Tony. Why was the collapse time three to four seconds longer than what it would take a 110-story steel-framed skyscraper to fall through air?? Huh?? Huh??!!? Answer that one!
 
Last edited:
Yeah, that's right. Twoofers believe that fire can't cause structural elements to fail. You nailed it.




Oooo... Hey everyone, Carlos here can tell us how structural redundancy engineered throughout a 47-storey steel-framed highrise became an "unstable mechanism". Finally! Oh boy! I'm looking forward to hearing this explanation!




Yaaah, Tony. Why was the collapse time three to four seconds longer than what it would take the building to fall through air?? Huh?? Huh??!!? Answer that one!

I think the answers are ”jooze”, right?
 
Yeah, that's right. Twoofers believe that fire can't cause structural elements to fail. You nailed it.


So?

Oooo... Hey everyone, Carlos here can tell us how structural redundancy engineered throughout a 47-storey steel-framed highrise became an "unstable mechanism". Finally! Oh boy! I'm looking forward to hearing this explanation!


When a structural elements fails there's a reduction of this redundancy.

Do you think redundancy is always the same regardless of the integrity of the structure?


Yaaah, Tony. Why was the collapse time three to four seconds longer than what it would take a 110-story steel-framed skyscraper to fall through air?? Huh?? Huh??!!? Answer that one!


I would say 4 or 5 seconds (at least), that means 40%-55% longer FFA time. Do you think it is not significant?
 
Yeah, that's right. Twoofers believe that fire can't cause structural elements to fail. You nailed it.




Oooo... Hey everyone, Carlos here can tell us how structural redundancy engineered throughout a 47-storey steel-framed highrise became an "unstable mechanism". Finally! Oh boy! I'm looking forward to hearing this explanation!




Yaaah, Tony. Why was the collapse time three to four seconds longer than what it would take a 110-story steel-framed skyscraper to fall through air?? Huh?? Huh??!!? Answer that one!
ergo, what do you mean by redundancy? How many column 79s were there? If it fails, what's next?
 
I say "Clunkity-Clunk" in 1,5 seconds, so the building should have collapsed in 1,5 x 110 = 165 seconds = 2,75 minutes

:D
 
Yeah, that's right. Twoofers believe that fire can't cause structural elements to fail. You nailed it.
Because they lack knowledge? Why can't 911 truth do anything beside rip off people and lie?

Oooo... Hey everyone, Carlos here can tell us how structural redundancy engineered throughout a 47-storey steel-framed highrise became an "unstable mechanism". Finally! Oh boy! I'm looking forward to hearing this explanation!
You never read NIST and offer no evidence to support your claims. Like 911 truth, failure to make a point. Go ahead explain what NIST got wrong.

Yaaah, Tony. Why was the collapse time three to four seconds longer than what it would take a 110-story steel-framed skyscraper to fall through air?? Huh?? Huh??!!? Answer that one!
Momentum - it is physics, you don't do physics.
http://www.internationalskeptics.com/forums/showpost.php?p=6263596&postcount=621
http://www.internationalskeptics.com/forums/showpost.php?p=8217097&postcount=49
You could do a model; why not? Math?
 

Exactly. You nailed it. No further discussion necessary.


When a structural elements fails there's a reduction of this redundancy.

Gosh, I never thought of this. This makes it all so clear! When a (or some?) "structural elements" fail, there is a reduction in redundancy. Wow.


I would say 4 or 5 seconds (at least), that means 40%-55% longer FFA time. Do you think it is not significant?

No, I totally agree with you. 110-storey furnished, steel-framed highrise buildings, with a heavily redundant steel core structure, concrete flooring and in some cases concrete partitions, should only take about 4 - 5 seconds to completely collapse while also pulverizing themselves beyond recognition. Discounting, of course, the time it takes to fall to the ground. Yup, 4 - 5 seconds should cover it. You nailed it again. Wow.
 
Last edited:
ergo, what do you mean by redundancy? How many column 79s were there? If it fails, what's next?

Oh my god, I don't know. What could possibly exist outside of column 79?? Is the number '79' part of a sequence of other structural columns, or does '79' in this case mean "THE column. The column upon which all else rests. DO NOT TOUCH." ?
 
Tony,

When I asked you about the assumptions built into your "solutions", you facilely & unimpressively answered "the same assumptions that NIST used."

I can assure you that you are wrong about even this vapid non-response.


tfk said:
1. Please draw the stress-strain curves (one curve for each temperature) implied by your values for E(Temp) from a strain of zero up to the max strain that you think is appropriate for your assumptions. (The assumptions that you haven't provided yet.)

Here they are.

picture.php


Note well that the equation that you used assumes that the correct stress strain curve is the dashed lines on the left of the graph.

The fact that, when materials creep yield due to temperature, they are no longer operating in the linear mode. You'd need to calculate the stress conditions at each point in the beam to figure out if the material could actually support that stress level at that particular temperature.

To the extent that any particular element was shown to not be able to support the stress assumed by the linear analysis, your results will be wrong.

tfk said:
2. Do you see any problem with using end constraints of "simple supports" for very low temps?

picture.php


Yes, at low temps, the bolts haven't broken. They are therefore holding the ends of the beam such that the slopes of the beams (∂y/∂x) are zero. This results in a completely different curve shape than the simply supported beams, which allows there to be a non-zero slope at the ends. This changes the solution of the "boundary condition differential equation", because the boundary conditions are not met.

The proper solution is to use a "fixed support / fixed support" at 20°C (before the bolts break), a "fixed support / simple support" for when one bolt breaks, and a "simple support / simple support" after both bolts break.


tfk said:
3. Why did you not build your model considering construction loads?

This is highly significant, because with the construction loads considered, you'll START your thermal deflections from an outer fiber stress state in your beams that is (for a factor of safety of 2) somewhere between 50% & 100% of yield strength in the beams, depending on the engineers' design criteria.

As you can see from the stress-strain curves above, even a conservative design loading will cause the outer fiber stress to drop considerably when heated, and cause the outer fibers to elongate dramatically.

Even in a rectangular cross-section beam (like the concrete), the loss of stress carrying capability in the outer fibers cause the fibers towards the neutral axis to assume stresses that are much, much higher than they would have to if you were still in the linear stress/strain range, because the outer fibers (with their high "moment arm" from the neutral axis) are the most efficient at counteracting the externally applied moments.

As the heat soaks into the beam, the inner fibers can also no longer support the necessary stresses, and the whole situation cascades in a positive feedback loop.


picture.php


Note that the tensile strength of the concrete is much lower than the compressive strength, and this causes the neutral axis to shift towards the upper surface.

But the situation in an I-beam is far, far worse than described, because of the cross-section. The load carrying capability of the web is insignificant compared to the load carrying capability of the upper & lower flange, simply due to the webs thin width. Once the outer fiber start yielding, then there is way too little material in the web to take up the load shed by the outer fibers.

picture.php


tfk said:
4. What are the underlying assumptions associated with the deflection curve for distributed load equation that you used? Paying primary attention to where the equation breaks down & gives wrong answers.

The important assumptions of this solution are the following:

a. You are staying within the linear stress-strain region.
This is wildly violated for your analysis.

b. Plane sections stay planar.
This is violated for your solution.

c. Boundary conditions are as stated above.
y0 = yL = ∂x/∂y0 = ∂x/∂yL = 0

One or both of your slope boundary conditions are violated, depending on how many bolts are fractured.

d. The beams are carrying all of the load.
This is significantly violated.

As soon as the beams START to yield from heat (i.e., without any physical deflections), they are going to shed their load back into the concrete, because 1. the concrete is also a solid beam, but a much, much wider one and 2. the concrete heats up much much slower than the steel.

This changes your load condition on the beams HUGELY. Their load fairly quickly will drop to self-weight, if the concrete can support itself over those spans.

tfk said:
5. What is the fundamental theoretical justification used in the generation of the distributed load equation that you used?

Cripes, Tony. This one was a bone that I threw you, and you still couldn't get it.

It's "Newton's 3rd law".

You guys are so fond of saying this in vapid meaningless contexts, yet the one time that it was appropriate, you drop the ball...?

One might come to the conclusion that you don't understand the flexure of beams at any deep level.

Not very good, Tony.

Why don't you gather back a couple of shards of engineering dignity & explain to everyone exactly how this equation is based on Newton's 3rd? Or would you rather that I did that for you, too?
___

The ultimate conclusion from all of the above is that, for the highly complex, high strain, & highly non-linear conditions that occur in beam sagging due to heating, the simple beam equations that are applicable to low stress & low strain are WILDLY inappropriate.

And that a competent FEA is the only way to get accurate results.

And this, right here, is my main message when looking at your spreadsheet, based on equations used, & assumptions made, that are wholly inappropriate for the analysis intended.

Is that "engineer-y" enough for ya, Tony?
Or does it still sound like "sales" to you?

Tom
 
Last edited:
Exactly. You nailed it. No further discussion necessary.


So, do you agree fire can cause a building collapse?

Gosh, I never thought of this. This makes it all so clear! When a (or some?) "structural elements" fail, there is a reduction in redundancy. Wow.


What do you think happens when there is no redundancy?

No, I totally agree with you. 110-storey furnished, steel-framed highrise buildings, with a heavily redundant steel core structure, concrete flooring and in some cases concrete partitions, should only take about 4 - 5 seconds to completely collapse


Who said 4-5 seconds to completely collapse?

while also pulverizing themselves beyond recognition.


This is what happens to buildings that fall in this way. For example:

http://www.internationalskeptics.com/forums/showthread.php?t=199290
 
Yes, this does look impressively engineery. But there are still some questions you don't seem to want to answer:

The important assumptions of this solution are the following:

a. You are staying within the linear stress-strain region.
This is wildly violated for your analysis.

How so?


b. Plane sections stay planar.
This is violated for your solution.

How so?


c. Boundary conditions are as stated above.
y0 = yL = ∂x/∂y0 = ∂x/∂yL = 0

One or both of your slope boundary conditions are violated, depending on how many bolts are fractured.

How so?


Cripes, Tony. This one was a bone that I threw you, and you still couldn't get it.

It's "Newton's 3rs law".

You guys are so fond of saying this in vapid meaningless contexts, yet the one time that it was appropriate, you drop the ball...?

I'm so sure this is true. Bedunkers have a such a deep understanding of Newton's Third Law, after all... ;)
 
Oh my god, I don't know. What could possibly exist outside of column 79?? Is the number '79' part of a sequence of other structural columns, or does '79' in this case mean "THE column. The column upon which all else rests. DO NOT TOUCH." ?

LMFAO.

And this is what ergo thinks constitutes for engineers a competent "numerical analysis" for WTC7.

"... hey did any of you guys notice that there are numbers other than 79?"
 
So, do you agree fire can cause a building collapse?

No, I'm agreeing with you that twoofers don't understand how "structural elements" can fail in fire.


What do you think happens when there is no redundancy?

Gosh, I don't know. Could you perhaps explain how you went from "hyperstatic" to "no redundancy"? Thanks!!


Who said 4-5 seconds to completely collapse?

Nobody said that. I'm completely agreeing with you that only 4 - 5 seconds of additional descent time is needed to explain the momentum losses through successive collisions through 80 - 90 storeys, and concomitant total pulverization of all contents and floor structures. Natch.
 
Yes, this does look impressively engineery. But there are still some questions you don't seem to want to answer:

How so?

How so?

How so?

All three were explained in my post. 2 of the 3 were explained & graphed.

Your ignorance doesn't change that.

If anyone of consequence asks, I'll be happy to explain.
You don't make that list.

I'm so sure this is true. Bedunkers have a such a deep understanding of Newton's Third Law, after all...

I explicitly offered Tony a chance to explain that.

I'll wait for him to fail to do so.

Then I'll do it for him.

tk

PS. Meanwhile, go hump somebody else's leg.
 