"Since the New York City regulations had a limit of one day tank up to 1.25 m3 (275 gal) per floor, and
since the base generators located on the 5th floor already made use of a 1.25 m3 (275 gal) day tank, the
Salomon Brothers system used a pressurized fuel distribution system, in which the pumps continuously
circulated fuel whenever the generators were running. There was enough fuel (160 L, 35 gal) stored at
pressure in the valve rig and piping located on the ceiling near the northeast corner of the 5th floor (Figure
3-1) to start the diesel engines, which, in turn, would supply power to operate the circulating pump. The
maximum fuel flow was 5.3 L/s (70 gal/min) at 340 kPa (50 psi)."
No day tank around 79. supplied directly from the first floor tanks.