The Parque Central was a 56 storey government office building in Caracas, Venezuela. The fire started on the 34th floor and climbed to the 47th floor. That's not similar to the WTC 7 because the fires were on the lower levels. The building didn't have a tube in a tube design like any of the WTC buildings either.
The single most important difference are in the columns.
The reinforced concrete structure consists of perimeter columns connected by post-tensioned concrete “macroslabs” that are each 10 feet (3 meters) deep and above the second–floor mezzanine, the 14th, 26th, 38th, and 49th floors. There’s no central core.
Individual floors between the macroslabs have a steel-deck floor supported by steel beams, all protected underneath with spray-on Cafco Blaze Shield DC/F mineral glass fiber wool with cement fireproofing. According to Cafco’s Manny Herrera, the floor was designed to meet U.S. standards for a two-hour fire resistance rating. However, the overall fire compartmentalization of each floor slab was decreased by the addition of several unrated floor panels to provide access to mechanical and plumbing systems.
Five structural bays rest on four lines of columns in each direction supporting the steel deck. In effect, the concrete structure includes five stacked steel buildings, each supported by a macroslab. During the fire, two steel decks partially collapsed; other than that, there was no collapse inside the building. However, deflection in some steel beams was severe.
The fire was also aggressively fought for a period of time.:
Commanders at the scene decided to bring a 2-inch (63-millimeter) hose line, fed by fire engines at the ground level, all the way up one of the fire stairs. Two portable booster pumps, each flowing 264 gallons per minute (gpm) at 58 psi (1,000 liters per minute [lpm] at 4 bar), were used to provide adequate pressure above the fire floor.
At approximately 1:15 a.m., firefighters working with two 1-inch (38-millimeter) hose lines from different locations above the 34th floor were able to slow the upward movement of the fire considerably. By 3 a.m., a second 2-inch (63-millimeter) hose line, identical to the first one, had been put into service, and firefighters confined the fire to three to four floors above the 34th floor. This approach was successful through the first five or six hours of the fire, when the fire spread vertically at a rate of approximately one floor every three hours. The 27th floor became the main staging area for about 100 firefighters.
At 7 a.m., some of the booster pumps started to malfunction, and the fire regained intensity, spreading vertically at a rate of about one floor per hour until approximately 10 a.m. Around 11 a.m., the fire breeched the fifth macroslab, below the 39th floor, and around noon, the stairwells’ fire enclosure started to fail. Concerned that the building might collapse, the fire chief immediately ordered that interior firefighting operations be abandoned. It should be noted that the CFD only reported minor injuries among its personnel during this risky operation.
The fire continued to move upwards through the afternoon, at a rate of about 2 1/2 floors per hour. Between 2 and 3 p.m., the Venezuelan government began using helicopters with water buckets, commonly used on forest fires, in an unsuccessful attempt to slow the fire down.
The fire eventually burned itself out at 3 a.m. on Monday morning, after spreading and consuming the contents of some 17 floors, more than 24 hours after it began.
Conclusion
Past history and performance shows that this fire could probably have been controlled quickly by a standard wet-pipe sprinkler system and that the fire department’s chances of controlling the fire at, or a few floors above, the floor of fire origin would have increased if the standpipe system had been working. This fire highlights the importance of periodic inspection, testing, and maintenance of fire protection systems, as well as the importance of strictly following manufacturers’ installation instructions.
This incident once again reminds us of the fire safety challenges high-rise buildings present and demonstrates that no fire department, no matter how large, professional, and well-equipped, can effectively control a fire without properly designed passive and functioning active fire protection systems. The CFD performed admirably in an impossible task, and its commanders made difficult decisions that ultimately proved to be the correct ones.