You just showed a figure showing that there is no connection damage vertically between the C44-79 girder and column 79, and you still cannot work out if the girder has walked off or not at that point???
You're not paying attention.
The figure shows that there IS connection damage vertically between the C44-79 girder and column 79.
In my image, the vertical damage IS there. Here it is again for you to see:
Don't you see that BLACK dot in the connection between C79 and A2001?
I'll zoom it in for you. This zoomed crop is from the BOTTOM image, the one showing damage in the VERTICAL direction.
See it now? Or do you need more zoom?
Now, that black dot is only in the FINAL report. I checked and saw that it's not in the DRAFT report, which is what made me wonder if adding the black dot in the FINAL report was a mistake (as the diagrams are clearly different, and if they were converted by hand, such a slip is possible), or if the connection had actually already failed vertically at 4 hours of simulation. I'm leaning towards the latter: I think most likely it is not a mistake. NIST says so in the report: "By 4.0 h of heating, [...] The girder between Columns 44 and 79 had walked off the bearing seat at Column 79 on Floor 13 [...]"
Look again at the figures that you posted. There is NO CONNECTION DAMAGE horizontally or vertically at EITHER END of girders A2015 and A2002 which both restrain column 79. Column 79 cannot move laterally without damaging the connections at C79, C76 or C80 in some combination.
I don't see A2015 in the framing plan you posted. Do you mean the girder between C76 and C79? That's the one that
pushed C76 to the west and C79 to the east when it expanded, according to NIST, so the status of its connection is mostly irrelevant. As for the one between C79 and C80, namely A2002, you're wrong. The beams that were supposed to restrain it from moving east (D3004, B3006, A2005, M3004) were either buckled or their connections failed both horizontally and vertically. Look at the picture again. See the beam to the southeast of C79? That's D3004. See it's coloured
pink? Now look at the legend. What does a
pink line mean? Yes, that's right: Buckled member. Now look at the connections of the others, both vertical and horizontal. What do they tell you?
Girder A2002 could move horizontally freely, letting the column move east as the girder between C76 and C79 expanded, as NIST said it happened. And let's not forget that A2002
was buckled anyway.
You have posted 2 figures that prove that column 79 has not moved laterally at the stage you are claiming that it did.
How do these figures show what you claim they show?
I think they show the exact opposite. Not the exact opposite, sorry. That was hyperbole. They don't prove that the column moved laterally, but they do prove that the column could move laterally if pushed by the girder to its west.
my emphasis
Is that the "one to the west" that shows "no connection damage" at either end?
So do you now accept that there is no lateral movement in the girder at this point? This is the clearest way I can think of putting it to you.....
[qimg]http://www.internationalskeptics.com/forums/attachment.php?attachmentid=32564&stc=1&d=1424626290[/qimg]
The connections that are circled that show "no connection damage", indicate that the girder remains constrained and has experienced no lateral shift to the East or anywhere else.
Frankly, I don't see what is so hard to understand. The girder expanded and pushed C76 to the west and C79 to the east. The girder did not experience any lateral movement other than that of its ends in opposite directions due to thermal expansion. The connections didn't need to fail for that to happen. NIST says such a movement happened. Pay attention.
This is the clearest way I can think of putting it to you:
THE BUCKLED GIRDER A2002 WAS FREE TO MOVE LATERALLY AND COULD NOT RESTRAIN C79. THE GIRDER BETWEEN C76 AND C79 EXPANDED DUE TO HEAT PUSHING C76 TO THE WEST AND C79 TO THE EAST, IRRESPECTIVE OF THE STATE OF ITS CONNECTIONS.
Got it now?