How do you reconcile that with the actual deflections measured by NIST on sample floor assemblies?
"The test was stopped at 116 min when, after another sudden drop, the center span deflection reached about 15in."
NCSTAR1.6, page 44, describing tests on a 35 foot restrained span with 3/4" SFRM. Given that the actual floor trusses were longer than this, and may have had damage to the SFRM, a deflection of 40" under normal loading doesn't seem inconsistent with this result.
It would be helpful if you could describe the basis of your calculations.
Dave
The results for a 700 degree C temperature and 88 lbs./sq. ft. floor loading are below.
Temperature (degrees C) = 700
Span (ft.) = 60
Floor load (lbs./sq. ft.) = 88
% of room temp MOE for concrete at temperature = 43
% of room temp MOE for steel at temperature = 64
Concrete MOE (psi) = 1.81E+06
Steel MOE (psi) = 3.00E+07
Concrete MOE at temp (psi) = 7.78E+05
Steel MOE at temp (psi) = 1.92E+07
Concrete slab thickness (in.) = 4
Slab centroid to top chord (in.) = 2.414
Top chord to bottom chord (in.) = 28.05
MOE ratio of steel to concrete = 2.47E+01
Effective slab width (in.) = 74.18
Transformed slab section area (in^2) = 1.20E+01
Top Chord area (in^2) = 3.25
Bottom Chord area (in^2) = 6.94E+00
Composite centroid distance from bottom (in.) = 2.1078E+01
Moment of Inertia double truss (in^4) = 4.30E+03
Deflection of main trusses (in.) = 2.08E+00
I can send you the spreadsheet if you like.
The calculations take into consideration the effect of temperature on the modulus of elasticity of both the concrete and steel in the composite beams.
I believe there is even something in the NIST report about a 2 inch deflection at 700 degrees and then later there is a lot of mumbo jumbo and viola we get 25 inches which is then expanded to 40+ inches by creep. The only way to do this is to apply additional loading and the only way that could have happened is for the load from disconnected trusses to be applied to a remaining connected truss.
As for the floor assembly testing you don't say what the concrete and steel temperatures and floor loading were. You need to do that.