You have claimed on the "gravity collapse" thread that:

Heiwa said:
All steel structure is designed with FoS > 3.

Secondly, the towers have great redundancy. You can remove parts of perimeter walls, core structure and floors anywhere and nothing happens except local falures! Example - a plane slices a perimeter wall and damages core structure and floors.

Thirdly, if you read my articles carefully you find a fair amount of structural calculations to confirm above and the stability of the parts. Also is described the step by step method to do proper structural damage analysis, the latter which neither NIST nor Bazant & Co has done.

When challenged for a detailed analysis of this, you cross-referenced your own paper wherein it is noted:

Heiwa said:
The above is a clear indication how the Towers were originally built by serious architects and engineers in the 1960's. Compressive static stresses in the primary structure columns were less than 1/3 of the yield stress of the steel before (obviously) ... and after serious damage (not so obvious but shown here)! The buckling stress of the column is virtually the same as the yield stress as the columns were arranged with spandrels. One reason why the static stresses were so low was that the designers had no access to computers to optimize (slender down) the construction. Manual calculations were done and to be on the safe side you added steel and built strong! And steel was quite cheap at that time. And US steel was good quality. The assumed yield stress 248 MPa was probably much higher in reality. NIST never checked the yield stress of the steel from the initiation zone in the rubble!

There was therefore plenty redundancy. A plane may crash into the bird cage and nothing happens. A big fire may break out and nothing happens. Why? Because the normal compressive stress in the supporting vertical structure is so low and if any column breaks or buckles, its load is transmitted to adjacent columns via the spandrels and the stress in adjacent columns increase a little. No global collapse is possible under any circumstances.

Evidently the columns got stronger (thicker plates, steel with higher yield stress) further down when the 'mass above' increases, but it is certain that the compressive stresses in the Towers never exceed 1/3 of the yield stress. Same applies for the buckling stresses.

I believe this analysis to be insufficiently detailed and, in particular, incorrect.

NIST tested the steel recovered from WTC (which in itself is of interest, as CTers usually claim it was all whisked away to China with unseemly haste). NIST NCS STAR 1-3D (http://www.fire.nist.gov/bfrlpubs/fire05/PDF/f05158.pdf) confirms a range of actual values:

- Core webs ranged from as low as 31.1 to 41.9 ksi, ie. 86 to 116% of specificed strength.

- Core flanges ranged from 32.4 to a high 53.4 ksi, ie. 90 to 146% of specified strength.

Setting to one side the 31.1 and 32.4 ksi results, inasmuch as a small proportion of columns below failure point are unlikely to lead to any wider problem, let's take the lower maximum of 116% specified value.

Now, the NIST Demand to Capacity Ratios (DCR) are based upon specified strengths and NIST themselves note that there is effectively spare capacity up to actual (but varying) yield point/strength.

Core columns in WTC typically had a Demand to Capacity Ratio (DCR) of 0.83, ie a safety factor of 1/0.83=1.20. Now let's assume assume that the steel has an additional 16% beyond minimum yield value. This would reduce the DCR to 1.16/.83=1.4.

In other words we could increase the loads in these areas by up to 40% before yield point was reached and plastic (permanent) deformation begins. Of course this figure has lots of variables - most of the steel webs did not have such a high yield factor, some areas had DCRs well in excess of 0.83, and so on.

What we don't do is then add any significant additional allowance for tensile strength because (a) yield failure is already occuring and (b) gravity loads will be compressive, not tensile.

As I frequently mention elsewhere on the forums, one thing we also have to appreciate is that the structure of WTC is complex; in addition to dead and live loads, it will be dealing with (for example) transverse and shear loadings from the wind. There will be a degree of torsion due to differential loading. And so on. We would therefore have to look at the exact steelwork design in considerable detail before we could determine a safety factor for each. That's why engineers earn a lot of cash, and why complex modelling software was developed.

Nevertheless it is clear that the actual capacity of the core is not going to be anything like 300% or 3:1 before irreversible damage and failure begin to occur.

But in any event the above calculations all assume an intact core, and we know from the various NIST studies and eyewitness evidence that the cores suffered damage - around a third. This will obviously have reduced loadbearing capacity still further, and a simple pro-rata reduction of (say) 30% is likely to be wrong because the damage is concentrated in localised areas and hence these areas will be susceptible to accelerated failure under loads.

Now, Heiwa, can you produce similar calcs and figures to back up the "FoS>3" position you've adopted, or is it as substantial as your structural calculations?
 
You're asking Heiwa for calcs? You are quite the optimist!
 
Specifically I'm asking for competent, detailed structural calculations. Not broad generalisations and irrelevent sweeping metaphors.
 
Specifically I'm asking for competent, detailed structural calculations. Not broad generalisations and irrelevent sweeping metaphors.
But that's all the entire truth movement have. I bet this thread is ignored or you'll get some dross posted.
 
Based on the current "fires" thread I'm going to go for "ignored". But that then allows me to cast it back at them later. And you never know, Heiwa might meander along.
 
Just to be clear, you're asking for calculations from the guy who once said this:

Weight (kg) or load (kg) = mass (kg). Yes, I am an engineer. What are you?

Ever get the feeling you're dealing with a guy who brought a teddy bear to a gunfight?
 
And the guy who believes that Newton's horse can never move the stone, because action equals reaction?
 
Now now, lads. Let Heiwa stand, or more probably fail, on the basis of how he responds to this. If he does. But don't hold your breath for a cogent, reasoned response.
 
Specifically I'm asking for competent, detailed structural calculations. Not broad generalisations and irrelevent sweeping metaphors.

Well if this is not the ultimate compliment I don't know what is. Heiwa's very own forum. I hope you have not bitten off more than you can chew Architect.
 
Last edited:
We'll see, Bill, we'll see. Now have you anything to bring to the table on this subject yourself?
 
We'll see, Bill, we'll see. Now have you anything to bring to the table on this subject yourself?

On this narrow a subject ? No, I don't think so. I will follow it with interest though. Well...perhaps an occasional comment.
 
Well Bill, that's more than Heiwa seems to be doing. Despite posting elsewhere on the site, he's carefully avoiding this thread. I'd be very interested to know why this might be.
 
Thanks for starting a thread with:

Heiwa

You have claimed on the "gravity collapse" thread that:


Originally Posted by Heiwa
All steel structure is designed with FoS > 3.

Secondly, the towers have great redundancy. You can remove parts of perimeter walls, core structure and floors anywhere and nothing happens except local falures! Example - a plane slices a perimeter wall and damages core structure and floors.

Thirdly, if you read my articles carefully you find a fair amount of structural calculations to confirm above and the stability of the parts. Also is described the step by step method to do proper structural damage analysis, the latter which neither NIST nor Bazant & Co has done.


Evidently I have never suggested that all steel structure is designed with FoS > 3. For certain items (subject to wear) you can use FoS = 6. For others you use FoS = 1.5.

Why do you start a new thread with a false quotation?

It is correct that WTC 1 structure had great redundancy. Remove 60% of all columns in a wall between 5 floors anywhere, bits of the floors inside these columns and some core columns and ... the tower still stands! Easy to prove.

It is also correct that NIST doesn't know how to do structural damage analysis. They can hardly do structural intact analysis!!

Example! When WTC 7 upper structure floors 16-47 free falls for 2.25 seconds and is only subject to small air resistance forces, NIST suggests that strong steel elements fail! It is not possible. Air resistance loads cannot break a steel element ... in free fall. Easy to prove!

What to do want to discuss? My articles on the Internet? Just copy/paste what you cannot understand and I will explain. In that way I will not get misquoted!
 
for convenience, this is the post in question

http://www.internationalskeptics.com/forums/showpost.php?p=4481512&postcount=1851




Thanks for starting a thread with:

Heiwa

You have claimed on the "gravity collapse" thread that:


Originally Posted by Heiwa
All steel structure is designed with FoS > 3.

Secondly, the towers have great redundancy. You can remove parts of perimeter walls, core structure and floors anywhere and nothing happens except local falures! Example - a plane slices a perimeter wall and damages core structure and floors.

Thirdly, if you read my articles carefully you find a fair amount of structural calculations to confirm above and the stability of the parts. Also is described the step by step method to do proper structural damage analysis, the latter which neither NIST nor Bazant & Co has done.


Evidently I have never suggested that all steel structure is designed with FoS > 3. For certain items (subject to wear) you can use FoS = 6. For others you use FoS = 1.5.

Why do you start a new thread with a false quotation?

It is correct that WTC 1 structure had great redundancy. Remove 60% of all columns in a wall between 5 floors anywhere, bits of the floors inside these columns and some core columns and ... the tower still stands! Easy to prove.

It is also correct that NIST doesn't know how to do structural damage analysis. They can hardly do structural intact analysis!!

Example! When WTC 7 upper structure floors 16-47 free falls for 2.25 seconds and is only subject to small air resistance forces, NIST suggests that strong steel elements fail! It is not possible. Air resistance loads cannot break a steel element ... in free fall. Easy to prove!

What to do want to discuss? My articles on the Internet? Just copy/paste what you cannot understand and I will explain. In that way I will not get misquoted!


Evidently I have never suggested that all steel structure is designed with FoS > 3.

err that's exactly what you said in your post:boggled:

All steel structure is designed with FoS > 3.

It may not be exactly what you meant, but it would be helpful if you say exactly what you mean (be specific). I assume that you're saying that Architect is taking your quote slightly out of context?

Perhaps there is a slight language barrier? (i'm assuming that English is not your native language).

No disrespect is intended.
 
for convenience, this is the post in question

http://www.internationalskeptics.com/forums/showpost.php?p=4481512&postcount=1851









err that's exactly what you said in your post:boggled:



It may not be exactly what you meant, but it would be helpful if you say exactly what you mean (be specific). I assume that you're saying that Architect is taking your quote slightly out of context?

Perhaps there is a slight language barrier? (i'm assuming that English is not your native language).

No disrespect is intended.

Yes, all steel structure elements (of WTC1 - generally the primary ones) that I have analysed in WTC 1 (listed in my article) have FoS>3, i.e. design stresses are very low. I assume reason for this is 1960's US building standards but I have not inquired further about that. Reason for FoS>3 is to provide redundancy, i.e. one or more elements may fail locally, while overall structure remains intact. One result of this is, e.g. that you can drop the upper structure part C on lower structure part A and only result is local failures of both parts in the contact interface and that part C remains on top of part A. Complete crush down of part A by part C is not possible and this I show in my articles.
If you read the complete articles you also find how the WTC structures were destroyed. Controlled demolition! I think I show that quite convincingly using my approach comparing with ship collisions. Others have done it better using other models and methods. Suggest you join AEtruth.org to ensure that a new, proper investigation is done.
 
Great, he shows up and then just lies about what he posted. What a waste of time.
 
Great, he shows up and then just lies about what he posted. What a waste of time.

Seems to be a pattern. It's the same with his two mile claim. He first said it then denied he said it then tried to explain it only to say it again then deny it...


He sure is proud of his award though.
 
Yes, all steel structure elements (of WTC1 - generally the primary ones) that I have analysed in WTC 1 (listed in my article) have FoS>3, i.e. design stresses are very low.

Please provide a source for this information, as I can determine no such detail in your paper (see quote above).

I assume reason for this is 1960's US building standards but I have not inquired further about that.

You've not researched the matter?

Reason for FoS>3 is to provide redundancy, i.e. one or more elements may fail locally, while overall structure remains intact.

With the deepest respect, we are quite aware of what safety factors are for. You have been challenged to provide evidence not that one was used during the design - that much is expected - but rather that it was greater than a factor of 3 especially inasmuch as the NIST test and modelling data seems to suggest something quite different.

One result of this is, e.g. that you can drop the upper structure part C on lower structure part A and only result is local failures of both parts in the contact interface and that part C remains on top of part A. Complete crush down of part A by part C is not possible and this I show in my articles.

If you read the complete articles you also find how the WTC structures were destroyed. Controlled demolition! I think I show that quite convincingly using my approach comparing with ship collisions. Others have done it better using other models and methods. Suggest you join AEtruth.org to ensure that a new, proper investigation is done.

This is not a thread about your proposed collapse mechanism, rather it is purely concerned with the technical detail of your claim regarding safety factors. I would ask that you please avoid such un-necessary derails.
 
Architect,

Factors of safety are meaningful only for the intact buildings. They are calculated with the REQUIREMENT that the components be intact, that the loads be directed as designed.

Once the building has started to "disassemble", once unplanned loads are applied, then the factor of safety of the original structure is completely irrelevant. It doesn't matter if it is 2, 20 or 200.

"How much extra load carrying capacity does our intact, undamaged building have over its expected loads?" is a completely different question than "What is the likelihood of collapse if we smash some fraction of the building?"

Architect, you alluded to this at the end of your first post.

A second massive error that Heiwa makes in his statement that "a smaller portion of the building can never crush down a bigger section" is to assume - incorrectly - that you can average the stress & strain energy over the entire structure. Doing this ignores (& eliminates) stress & strain energy concentrations that are key to progressive collapse.

tom
 