You have claimed on the "gravity collapse" thread that:
When challenged for a detailed analysis of this, you cross-referenced your own paper wherein it is noted:
I believe this analysis to be insufficiently detailed and, in particular, incorrect.
NIST tested the steel recovered from WTC (which in itself is of interest, as CTers usually claim it was all whisked away to China with unseemly haste). NIST NCS STAR 1-3D (http://www.fire.nist.gov/bfrlpubs/fire05/PDF/f05158.pdf) confirms a range of actual values:
- Core webs ranged from as low as 31.1 to 41.9 ksi, ie. 86 to 116% of specificed strength.
- Core flanges ranged from 32.4 to a high 53.4 ksi, ie. 90 to 146% of specified strength.
Setting to one side the 31.1 and 32.4 ksi results, inasmuch as a small proportion of columns below failure point are unlikely to lead to any wider problem, let's take the lower maximum of 116% specified value.
Now, the NIST Demand to Capacity Ratios (DCR) are based upon specified strengths and NIST themselves note that there is effectively spare capacity up to actual (but varying) yield point/strength.
Core columns in WTC typically had a Demand to Capacity Ratio (DCR) of 0.83, ie a safety factor of 1/0.83=1.20. Now let's assume assume that the steel has an additional 16% beyond minimum yield value. This would reduce the DCR to 1.16/.83=1.4.
In other words we could increase the loads in these areas by up to 40% before yield point was reached and plastic (permanent) deformation begins. Of course this figure has lots of variables - most of the steel webs did not have such a high yield factor, some areas had DCRs well in excess of 0.83, and so on.
What we don't do is then add any significant additional allowance for tensile strength because (a) yield failure is already occuring and (b) gravity loads will be compressive, not tensile.
As I frequently mention elsewhere on the forums, one thing we also have to appreciate is that the structure of WTC is complex; in addition to dead and live loads, it will be dealing with (for example) transverse and shear loadings from the wind. There will be a degree of torsion due to differential loading. And so on. We would therefore have to look at the exact steelwork design in considerable detail before we could determine a safety factor for each. That's why engineers earn a lot of cash, and why complex modelling software was developed.
Nevertheless it is clear that the actual capacity of the core is not going to be anything like 300% or 3:1 before irreversible damage and failure begin to occur.
But in any event the above calculations all assume an intact core, and we know from the various NIST studies and eyewitness evidence that the cores suffered damage - around a third. This will obviously have reduced loadbearing capacity still further, and a simple pro-rata reduction of (say) 30% is likely to be wrong because the damage is concentrated in localised areas and hence these areas will be susceptible to accelerated failure under loads.
Now, Heiwa, can you produce similar calcs and figures to back up the "FoS>3" position you've adopted, or is it as substantial as your structural calculations?
You have claimed on the "gravity collapse" thread that:
Heiwa said:All steel structure is designed with FoS > 3.
Secondly, the towers have great redundancy. You can remove parts of perimeter walls, core structure and floors anywhere and nothing happens except local falures! Example - a plane slices a perimeter wall and damages core structure and floors.
Thirdly, if you read my articles carefully you find a fair amount of structural calculations to confirm above and the stability of the parts. Also is described the step by step method to do proper structural damage analysis, the latter which neither NIST nor Bazant & Co has done.
When challenged for a detailed analysis of this, you cross-referenced your own paper wherein it is noted:
Heiwa said:The above is a clear indication how the Towers were originally built by serious architects and engineers in the 1960's. Compressive static stresses in the primary structure columns were less than 1/3 of the yield stress of the steel before (obviously) ... and after serious damage (not so obvious but shown here)! The buckling stress of the column is virtually the same as the yield stress as the columns were arranged with spandrels. One reason why the static stresses were so low was that the designers had no access to computers to optimize (slender down) the construction. Manual calculations were done and to be on the safe side you added steel and built strong! And steel was quite cheap at that time. And US steel was good quality. The assumed yield stress 248 MPa was probably much higher in reality. NIST never checked the yield stress of the steel from the initiation zone in the rubble!
There was therefore plenty redundancy. A plane may crash into the bird cage and nothing happens. A big fire may break out and nothing happens. Why? Because the normal compressive stress in the supporting vertical structure is so low and if any column breaks or buckles, its load is transmitted to adjacent columns via the spandrels and the stress in adjacent columns increase a little. No global collapse is possible under any circumstances.
Evidently the columns got stronger (thicker plates, steel with higher yield stress) further down when the 'mass above' increases, but it is certain that the compressive stresses in the Towers never exceed 1/3 of the yield stress. Same applies for the buckling stresses.
I believe this analysis to be insufficiently detailed and, in particular, incorrect.
NIST tested the steel recovered from WTC (which in itself is of interest, as CTers usually claim it was all whisked away to China with unseemly haste). NIST NCS STAR 1-3D (http://www.fire.nist.gov/bfrlpubs/fire05/PDF/f05158.pdf) confirms a range of actual values:
- Core webs ranged from as low as 31.1 to 41.9 ksi, ie. 86 to 116% of specificed strength.
- Core flanges ranged from 32.4 to a high 53.4 ksi, ie. 90 to 146% of specified strength.
Setting to one side the 31.1 and 32.4 ksi results, inasmuch as a small proportion of columns below failure point are unlikely to lead to any wider problem, let's take the lower maximum of 116% specified value.
Now, the NIST Demand to Capacity Ratios (DCR) are based upon specified strengths and NIST themselves note that there is effectively spare capacity up to actual (but varying) yield point/strength.
Core columns in WTC typically had a Demand to Capacity Ratio (DCR) of 0.83, ie a safety factor of 1/0.83=1.20. Now let's assume assume that the steel has an additional 16% beyond minimum yield value. This would reduce the DCR to 1.16/.83=1.4.
In other words we could increase the loads in these areas by up to 40% before yield point was reached and plastic (permanent) deformation begins. Of course this figure has lots of variables - most of the steel webs did not have such a high yield factor, some areas had DCRs well in excess of 0.83, and so on.
What we don't do is then add any significant additional allowance for tensile strength because (a) yield failure is already occuring and (b) gravity loads will be compressive, not tensile.
As I frequently mention elsewhere on the forums, one thing we also have to appreciate is that the structure of WTC is complex; in addition to dead and live loads, it will be dealing with (for example) transverse and shear loadings from the wind. There will be a degree of torsion due to differential loading. And so on. We would therefore have to look at the exact steelwork design in considerable detail before we could determine a safety factor for each. That's why engineers earn a lot of cash, and why complex modelling software was developed.
Nevertheless it is clear that the actual capacity of the core is not going to be anything like 300% or 3:1 before irreversible damage and failure begin to occur.
But in any event the above calculations all assume an intact core, and we know from the various NIST studies and eyewitness evidence that the cores suffered damage - around a third. This will obviously have reduced loadbearing capacity still further, and a simple pro-rata reduction of (say) 30% is likely to be wrong because the damage is concentrated in localised areas and hence these areas will be susceptible to accelerated failure under loads.
Now, Heiwa, can you produce similar calcs and figures to back up the "FoS>3" position you've adopted, or is it as substantial as your structural calculations?